industrial bonding gas..?

Joined
16 Feb 2007
Messages
11,795
Reaction score
482
Location
West Midlands
Country
United Kingdom
Just noticed at work yesterday that the main gas incommer ( big 6 inch pipe.. !!! ) is only "bonded" to the nearest board in 16mm² cable..

should this not be a bond back to the main earth for the installation which is about 50m away.. in the sub station ( we have our own transformer in there and the 11KV switchgear for the rest of the road.. along with the distribution chamber for or factory.. )

also, any idea what size it would have to be for that distance?
 
Sponsored Links
Not got BS7671 with me at the moment but you may need 25mm to keep resistance below 0.05ohms over 50M.
I think the maximum you can get with 10mm is 27M.
I'm sure somebody else will be able to check for certain.

Utilising structural steel is also an option under certain circumstances.
 
Yeah, though in an industrial installation the fault currents can be a lot higher than in a domestic, a lot depends on the size of the supply, iirc the 0.05ohm is derived from a 50v touch figure for a 100A supply.
 