Invertor welder went bang

Joined
31 Mar 2006
Messages
20,031
Reaction score
1,397
Location
Leeds
Country
United Kingdom
I was doing some welding in the workshop today using a cheap invertor welder.

It’s just a 13A plug in stick welder job.

Anyway I’m welding away and all of a sudden there was a loud bang from the end of the welding rod and all my electric went off.

Where the bang had happened there was some orange staining almost rust colour, and what ever happened managed to blow the plug fuse, trip the C32 local breaker and also the C50 submains breaker, as well as welding the MK socket switch in the on position. Fortunately it didn’t take the cutout which I think is an 80A BS88.

I’ve not taken the welder in bits yet but I’m wondering what could have caused this? I guess a biiiig current must have flown to take out all that circuit protection. Possibly somehow the welder has presented full mains voltage at the output cables? I’ll have to measure IPFC at this socket, and see if it’s high enough to take the magnetic trip on a C50.
 
Probably the isolation between the mains input to the invertor and the low voltage output failed thus putting the Live mains directly to the welding rod. A close shave for you.
 
Where the bang had happened there was some orange staining almost rust colour, and what ever happened managed to blow the plug fuse, trip the C32 local breaker and also the C50 submains breaker, as well as welding the MK socket switch in the on position. .... I guess a biiiig current must have flown to take out all that circuit protection. Possibly somehow the welder has presented full mains voltage at the output cables?
Frightening! Yes, as you and Bernard have said, that would seem to be the most likely explanation - or, alternatively, I suppose, simply a sudden L-N or L-E fault on the mains side of the inverter (for whatever reason) - but that would seem far less likely in view of what you observed at the welding electrodes.
I’ll have to measure IPFC at this socket, and see if it’s high enough to take the magnetic trip on a C50.
Yes, that would be interesting, albeit rather academic, because we know that a C50 (and a C32) did trip magnetically. I suppose that a C50 can trip magnetically with 'as little' as 300A, and that would only need a Ze of ≤0.77Ω at 230V, and in the 'worst case' of 500A being required, that would 'only' require ≤0.46Ω - neither of which is beyond credibility.

It will be interesting vto learn what you discover - I wait with bated breath!

Kind Regards, John
 
I’m not an electronics expert so I’m not sure what’s happened. Inside the only damage I can see is a little flash mark on these components.

They seem to be on a mains input board which supplies a bridge rectifier.

F39A906D-4A8E-4809-85DB-7BC84BDF44E5.jpeg

A931BD98-A21A-4002-990E-94915FE96B24.jpeg

2CBCB37D-C546-4CF2-9E9C-476739934B87.jpeg
 

Attachments

  • 2EAF4808-D4BD-4211-8BA7-6FBE11F85239.jpeg
    2EAF4808-D4BD-4211-8BA7-6FBE11F85239.jpeg
    381.1 KB · Views: 218
I’m not an electronics expert so I’m not sure what’s happened. Inside the only damage I can see is a little flash mark on these components. ... They seem to be on a mains input board which supplies a bridge rectifier.
No 'tracking'/damage on any of the PCBs?

Have you measured 'continuity' between mains input and the output of the inverter? ... and what about the L-N and L-E resistance at the mains input?

'Enough' PSC to magnetically trip a C50, at least!

Kind Regards, John
 
No I can’t see any sign of any damage at all apart from what’s in the photos!!

No I haven’t checked. I will do and let you know.
 
No, no damp at all. It had been working fine for a bit before it spat it’s dummy out.
 
With an inverter two things can cause high current, one the capacitor goes, and two it stops oscillating, as you know it turns AC to DC charges a capacitor and then turns DC to high frequency AC to allow a smaller transformer and smoother welding, if it fails to turn the DC to AC then the transformer becomes near a direct short.
 
35E48D6A-C903-4138-A689-EA1C0ADAF7E2.jpeg


Just done some more looking. It looks like something has flashed over here. I thought they look like MOVs but the symbol on the PCB looks like a capacitor? I really don’t know enough about electronics


Also I’ve been at it with the megger and everything tests >200MΩ L>E and N>E on the input, and also L input > both output terminals, and N input > both output terminals.

Also I have noticed that the plugtop fuse did NOT blow, just the MCBs!


Also I’ve managed to give my self a nice dose of sunburn today while using my good old transformer welder
263FEED4-F0BF-47C9-8D6C-577BB36E1996.jpeg
 
They do look like MOVs to me, should be able to identify the voltage rating from the side of the least burnt one. Cheap enough to replace. They short the supply by design to prevent voltage spikes, but I've found them to blow if the fuse doesn't trip soon enough.

I've repaired an inverter welder before and it was the output IGBTs which had failed shorted and had to be replaced.
 
They certainly look like MOVs to me, though as you say the legend on the PCB suggests they are capacitors, but I suspect that's not the case. I f you can confirm they are MOVs then this might be a suitable replacement

https://cpc.farnell.com/epcos/b72205s0381k101/varistor-13-5j-385vac/dp/RE03669?st=MOV

but check the quench current ratings of the original, a higher quench current might be needed. If so, look here:

https://uk.farnell.com/w/c/circuit-...-suppressors/tvs-varistors/prl/results?st=mov
 
Last edited:
They do look like MOVs to me, should be able to identify the voltage rating from the side of the least burnt one. Cheap enough to replace. They short the supply by design to prevent voltage spikes, but I've found them to blow if the fuse doesn't trip soon enough.
MOVs certainly often look like that (and, as you say, hopefully some markings might clarify) - although that obviously doesn't prove that they are! As you say, that could explain the trip, but it wouldn't explain what RF appeared to be describing as having happened at the business end of the welding electrodes - maybe that was just a red herring?

Kind Regards, John
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back