Is a 30A JB rated for 3 x 10mm conductors?

Joined
3 Jul 2007
Messages
4,134
Reaction score
166
Location
Manchester
Country
United Kingdom
:lol:

10mmjunction.jpg
 
Especially as they're useless!
1996 build, 10mm from MET to 30A JB, two outgoing 10mm to a kitchen sink and a utility sink.
Main water bonded elsewhere.

Same property (PME) had its main earthing conductor originating from an earth rod. Ze was 184 ohms - split load CU with half of the circuits without RCD protection!

PEB's (water and gas) terminated at the MET along with a 16mm main earth from the PME service head. Ze at MET was 0.24 ohms.

The 16mm from the earth rod to CU passed by the MET so I cut the cable and terminated both in the MET.

It seems to me that it's a TT converted to PME without the earthing being corrected at the time.
 
You know, there is no Reg that says a bonding conductor has to be unbroken.

However the assumption here is that in the event of fault current circulating in the bonds, the 30A rating of the junction box won't be exceeded for any length of time. :?

CPCs are broken all over the place :)
 
Yes I know though if I was going to extend a protective bonding conductor then it would only be by compression (10mm uninsulated crimp) and not a screwed terminal.

There's also the problem of poor connection. The terminal screw was in place by a single thread due to excessive amount of copper.
 
Gary, you're right about the crimp (and heat shrink/insulation). Or place two clamps on the pipe.

I did wonder how much 'bite' was on the JB screw.

It's a common complaint I know, but the way the major housebuilders crack the whip I'm surprised things aren't worse.

At least on this occasion there was some bonding.

Imagine if it was hidden. Continuity testing would prove all was OK. What ever happend to the high current test? :D
 