When the nominal voltage was arbitrarily reduced to 230 without changing the actual voltage, the values and calculation criteria must have taken this into consideration.I'm still not clear about this (as I said, never have been) - and your statement "...and calculations must allow for this" (in combination with your 'yes' answer) makes me even less sure.Yes, I believe that's what nominal voltage is even if the actual voltage is never that low. The figure chosen, although unrealistic, to be in-line with Europe and, as discussed before, all values and calculations must allow for this.There's also the question (to which I've never been sure of the answer) of whether the 'design current' of a circuit relates to what the current would be at nominal supply voltage, or whether it should take account of the maximum permitted supply voltage. I assume you think the former?
There's no need as it will be stated on the box, 7.5kW @ 240V, i.e. 7500/240 = 31.25A. That's what the shower is.If one has a shower rated at 7.5kW at 240V, when one calculates the 'design curent' for its circuit, does one do so {albeit invoving some guesstimating, unless one measures} assuming a nominal supply voltage of 230V
That's not using 240V as the nominal voltage. The MIs are telling you the current.
The fact that it works out at 30A @ 230V is immaterial as doing this would not be following the MIs. plus they will state that 32A CPD should be used.
That's not necessary either as that, too, must be allowed for in the figures.(which seems a bit odd, since that is in the 'non-safe' direction), or does one caluculate/estimate design current "allowing for" the fact that the supply current could, in fact, be as high as 253V (which seems the 'conservative'/'safer' approach)?