Is the BS3781 LOADMASTER SINGLE POLE MCB the same IEC60898,
24 Oct 2009
Hampshire
Is the BS3781 LOADMASTER SINGLE POLE MCB the same as IEC60898 as far as max Zs and disconnect times are concerned.
Do you have a copy of Guidance Note 3?
The type 3 breakers require 10x their rated trip value to disconnect within 0.1s as do type C breakers hence their max Zs values are the same.
why i did not look in Gn3 I don't know. Got hooked up on searching for the Bs number. Thanks guys :D