I noticed that my friend has had two double sockets added this way. Each double socket is connected straight back to one 32A MCB ie 2 very short radials. Nothing else is connected to this MCB. Does this comply.
Its an interesting one as there is a debate on it elsewhere that I was involved in.You could say it is not a recognised way of wiring a circuit, but it is no different to the spur off a ring final where it is assumed that the load will be max 26A drawn from a double socket (2.5 t+e 27A clipped direct)
If the install method has any reducing factors then it definately would not comply as the current carrying capacity of the cable could well be below 26A
Edit: I have assumed the cable is 2.5 t+e.If 4mm then the circuit will definately comply (unless install conditions are arduous)
As far as the overcurrent and fault current protection are concerned, subject to the normal circuit calculations I don't see why not, though I wouldn't consider this type of circuit best practice.