Just wanted to check the wiring on 2port valves,

so long as i connect live and neutral, the valve opens, (ie brown and blue), The Orange and Grey are effectivly in built switches to turn on something else - any voltage/current going through them would be whatever is put in at one end?
 
No

Blue is neutral
Grey is permanent live in
Brown is switch live in (from a programmer, for example)
Orange is switch live out (to a boiler, for example)
 
Yes

Grey and orange wires are connected to a microswitch
If you put 240 volts on grey, when valve fully open, 240 will appear on orange
If you put 1.5 volt in grey, that is what will be presented on orange when valve opens
If you connect your multimeter across grey and orange, you will see an open circuit until valve closes, when meter will show a short circuit
Switch may make before valve fully opened
 
If you connect your multimeter across grey and orange, you will see an open circuit until valve closes, when meter will show a short circuit
Are you sure about that?
Switch may make before valve fully opened
You are contradicting yourself.
 
Also remember that when operating the lever it only throws far enough to open the valve, it does not go far enough to actuate the micro switch.

Nozzle
 
Ops. Should read valve opens(n)
DH, when you read all the lines in my post, would you see the quoted line as a contradiction or mistype?
 
Just wanted to check the wiring on 2port valves,

so long as i connect live and neutral, the valve opens, (ie brown and blue), The Orange and Grey are effectivly in built switches to turn on something else - any voltage/current going through them would be whatever is put in at one end?

Yes that is all correct!

Two-port-Motorised-Zone-Valve.jpg
 
thanks for the responses, I would have wired a 2 port valve, but don't have a spare to try with!
 
Ops. Should read valve opens(n)
DH, when you read all the lines in my post, would you see the quoted line as a contradiction or mistype?
I quoted two part of your post. The first was incorrect - as you acknowledge above; the second was correct. This could have caused confusion to some readers.

"Open" is not a mistype of "close"; "chose" would be.
 
I quoted two part of your post. The first was incorrect - as you acknowledge above; the second was correct. This could have caused confusion to some readers.

"Open" is not a mistype of "close"; "chose" would be.
If there was a dislike button, I would have used that on above quote
Would you like me to do hundred lines 'I will read all my posts before posting?'

To confused readers, I apologise in advance for causing confusion :)
 