Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
hi, i want to use my extractor fan outlet as a vent for my cooker hood, can i turn the isolator switch into a socket for the supply to the hood.thank you.
It depends on what is upstream of the isolator switch. As it was for an extractor fan, I'd expect it was powered from a lighting cct. If it is the answer is no, unless you create a fused spur that will protect the rest of the cct from becoming overloaded and tripping the breaker/blowing the fuse if a heavier load is plugged in (after all, a socket can have a 3kW device connected to it!). The breaker/fuse will protect the cct wiring but it is risking constant trips. I would remove the plug and use one of these http://www.tlc-direct.co.uk/Products/MKK1070.html
fused suitably.
If it is via a fused spur from a power cct then you can go ahead as you plan.
Also, remember that the regs require there to be an accessible means of isolation within 2m of the unit, so you may need to include a DP switch upstream of the connection.
And, as it's in a kitchen, it is notifiable work, so the LABC or a self certifier need to be involved.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local