    While changing some socket fronts in our kitchen I've realized that there are some mixed cable sizes!

    2.5mm goes from the board to the first few sockets then it looks like 1.5mm from one to a few more then 2.5mm back to the board!

    There is absolutely no way for me to change the cable at the moment as it's a full rip out to sort it and were not planning on decoration any time soon.

    What's the best and safest solution?

    I was thinking of de-rating the MCB to 16a?
     
  2. Sponsored Links
  3. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,931
    Thanks Received:
    1,780
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Are you sure ring final, not spur off ring final?
     
  4. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,962
    Thanks Received:
    1,130
    Location:
    Dorset
    Country:
    United Kingdom
    Unless by some miracle the 1.5mm2 cable is pyro, you'll need to change things.

    As mentioned, is the 1.5mm2 DIRECTLY on the ring, or is it spurred in some way?

    If the 1.5mm2 forms part of the ring directly, you MAY be able to use a 20amp device - but more investigation required first.
     
  5. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    It's 100% a ring final and there are no spurs off any socket. Wouldn't it need to be a 16a breaker in order to provide protection of the length of 1.5mm that is in the ring?
     
  6. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,962
    Thanks Received:
    1,130
    Location:
    Dorset
    Country:
    United Kingdom
    Well, a ring wired fully in 2.5mm2 can be protected at 32amp,
    but a radial in 2.5mm2 is usually only protected by 20amp,
    so
    one could argue a ring wired in 1.5mm2 could be protected by 20amp as it's a ring; it's fed by two cables, electricity flowing two ways.

    Let's see what others think before you do anything.
     
  7. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,336
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
    Looks like it has been there a long time with no problems even if it does not comply with the (non statuary) regs. If it is near the centre of the ring it is unlikely to carry more than 20 amps anyway. Your choice, but I know what mine would be until redecoration.
     
  8. Steve

    Steve

    Joined:
    15 Apr 2005
    Messages:
    16,497
    Thanks Received:
    244
    Location:
    Yorkshire
    Country:
    United Kingdom
    All legs of a ring have to be capable of carrying 20A (this is a specific reg). This is why if you wire a ring reference method 101 (bungalows) you must use 4mm² cable or derate it to 20A.
     
  9. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,336
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
    1.5mm cable is rated at 20a I believe.
     
  10. Sponsored Links
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    It is - but 1.5mm² is not allowed by the regulation because it (the regulation) still caters for a 30A BS3036 fuse protecting the circuit.

    With a 32A MCB it would be fine.
     
  12. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    so would it be best to temporarily chance the MCB to a B20 or B16? until I can get it rectified
     
  13. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,336
    Thanks Received:
    571
    Location:
    London
    Country:
    United Kingdom
    That would require you to work on a live CU. Potentially more dangerous than leaving everything as it is.
     
  14. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    Only because the regulation still includes the likelihood that it might have a 30A BS3036 fuse.

    But it could be 25A.

    That's not an argument. If it were protected by a 20A MCB, it could just be a radial circuit.

    Therefore it has a capacity of 40A.
     
  15. chivers67

    chivers67

    Joined:
    18 Nov 2008
    Messages:
    1,472
    Thanks Received:
    186
    Location:
    Surrey
    Country:
    United Kingdom
    If you change it to a 16 A expect it to trip if the washing machine is on spin and someone puts a toaster & kettle on.
     
  16. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    How long has it been like it is?

    Is there any sign of overheating on the cables?
     
  17. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    few years at least, no obvious damage that I can see
     