We just moved into a house that had a pro re-wire, but the kitchen wasn't complete. 3 circuits labelled at the consumer - sockets/hob/oven. Cables into the kitchen are: 2x 2.5mm T&E(for the sockets ring I think) , and 2x fatter T&E labelled Hob and Oven. So I know what they're meant for ok, but there is also a heavy guage earth cable on its own? I'm running a 3.6KW oven plus halogen hob, would these need a dedicated earth or would the earth in the T&E be heavy enough? Thanks in advance :?
The Earth core in the cables feeding the circuits is more than sufficient for the tasks required of them, just ensure that they are sleeved in Green/Yellow sleeving.
The Large Earth core you have is likely to be a main bond, either from the Gas main in, or the Mains water in. If you have a Gas meter, check where the meter is and see if there is a cable clamped to the pipe on YOUR side of the meter.
Also, check where the water enters the building, there will be a stop-cock, within 600mm of this, again on your side of the stop-cock, should be an Earth connection.
Regardless of Gas/Water bond, if it is terminated at that end, then you simply need to terminate it in the spare Bond terminals of the Earth bar in the consumer unit..if it is not connected at the other end, then you need to ensure this is properly clamped onto the pipe using a BS951 EC15 Earth Clamp and crimp lugs.