The Electrician visited today... no success so far and he's going to start tomorrow by removing all sockets and doing testing that sounded like what you guys have described.
Just to answer a couple of things...
I turned on the outside lights and they work fine - so are on the OUTSIDE LIGHTS MCB.
I have already found and isolated the integrated fridge freezer - as mentioned by someone else - and am currently running that from a socket in the living room via an extension.
I am frustrated by the situation that each time the RCD trips it takes out the boiler... it obviously restarts, but I am always nervous about boilers, so I did ask him if it was possible to put the boiler onto its own RCBO - he implied it was indeed possible. If it is possible, I'd like to do that.
What he did that was different to me, was test the RCD itself, by turning off all MCBs, then pressing the yellow button and turning on all circuits one by one, until it tripped again on KITCHEN SOCKETS... he's satisfied there's nothing wrong there, but mentioned that test was telling him something about "earth leakage".
Oh, and he also checked behind the kitchen wall to ensure the room behind had no nails or screws in it - it hadn't, although we noticed a screw up by the coving in the living room (not within a "safe space" area) and I said to him that I thought a lot of wires do go places via the ceiling space rather than the floor - something to think about.
Beyond that he said the things I'd done so far, with guidance from here, were exactly what he would have done at the start... he reckons that it's something more fundamental. More to come, it seems.
Just to answer a couple of things...
I turned on the outside lights and they work fine - so are on the OUTSIDE LIGHTS MCB.
I have already found and isolated the integrated fridge freezer - as mentioned by someone else - and am currently running that from a socket in the living room via an extension.
I am frustrated by the situation that each time the RCD trips it takes out the boiler... it obviously restarts, but I am always nervous about boilers, so I did ask him if it was possible to put the boiler onto its own RCBO - he implied it was indeed possible. If it is possible, I'd like to do that.
What he did that was different to me, was test the RCD itself, by turning off all MCBs, then pressing the yellow button and turning on all circuits one by one, until it tripped again on KITCHEN SOCKETS... he's satisfied there's nothing wrong there, but mentioned that test was telling him something about "earth leakage".
Beyond that he said the things I'd done so far, with guidance from here, were exactly what he would have done at the start... he reckons that it's something more fundamental. More to come, it seems.