Hi everyone. Hope all is well. Wondering if i any sparkies could check the attached is correct? Recently started level 2 part time evenings.

Thanks
 

Attachments

  • IMG_5705.png
    IMG_5705.png
    1.1 MB · Views: 12
The ring circuit is not a ring! If it were a ring then there would be two conductors at the mcb, neutral and earthg bars.

Maybe its the way you have drawn it, but the ring starts and ends in the CU, not outside.

Think about it, and try again

PS What is the double pole device at the top of the two diagrams?
 
I was thinking that but the top sketch is like that aswell? Is the top sketch part of the question? Or did you do that?
 
Make it look like a ring final 1791899972753.pngI put in 6 sockets so you can't cut and paste. Get the words correct, get use to calling it a ring final, not just a ring, they are not the same.

It does not ask for a fused connection unit, so don't add one.
 
Excuse the messy lines but I will neat it up on fresh diagram if wiring looks ok now?
 