Loud bang sound when economy 7 meter switches over.

Discussion in 'Electrics UK' started by eveares, 5 Nov 2015.

  1. eveares

    eveares

    Joined:
    28 Jul 2012
    Messages:
    1,301
    Thanks Received:
    46
    Location:
    Surrey
    Country:
    United Kingdom
    My grandparents live a bungalow with modern central heating that has a economy 7/dual tariff meter that according to them is making a loudish bang sound when it switches over at night and in the morning.

    Note that they do not have any storage heaters or any other high night time loads and only the main consumer unit connected up to the meter. The economy 7 is simply left over and still active from the previous owners of the bungalow.

    Now their meter is simply a 2-rate meter with a LCD display. Now I presume the sound is some sort of switch/contractor in side the meter that is making the sound, but is it supposed to be loud/very noticeable?

    Also, is their any benefit of them being on a dual rate tariff?
     
  2. Sponsored Links
  3. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    If the sound is coming from the meter, that would worry me. They're also paying extra for their daytime usage on Economy 7, which is not generally worthwhile unless their night-time usage is more than 10% of their total usage. I suggest they contact their supplier and ask to come off E7, which will probably result in the meter being changed.
     
  4. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    46,696
    Thanks Received:
    3,013
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    True. However, I would add that my E7 system (I think the timeswitch, rather than the meter) makes an incredibly loud 'clunk' (which can be heard two or three rooms away) when it switches - and has done so for 25+ years.
    I agree. With most suppliers (certainly mine), you need at least 30%-35% of total usage to be at 'night rate' before E7 ceases to be more expensive than a standard 'single' tariff.

    Kind Regards, John
     
  5. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    My bills have reduced since coming off E7, in spite of the fact that we used to only use the dishwasher and tumble drier at night.
     
  6. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    46,696
    Thanks Received:
    3,013
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I'm not sure I understand the "in spite of only using ..." - I would have thought it was "because of only using ...". A DW and dryer are surely never going to use 30%+ of your daily total.

    Kind Regards, John
     
  7. PBC_1966

    PBC_1966

    Joined:
    1 Sep 2015
    Messages:
    2,409
    Thanks Received:
    210
    Location:
    Redding, California
    Country:
    United States
    Indeed - I had E7 for years at my last home in England and the sound of the contactor opening and closing could be heard a couple of rooms away when it was very quiet at night. As you say though, more of a loud "clunk" than a "bang," but people's descriptions of sounds can differ somewhat! With an older mechanical meter you can also hear the sound of the solenoid switching over the drive, but that's much quieter.
     
  8. phatboy

    phatboy

    Joined:
    22 Jan 2012
    Messages:
    2,119
    Thanks Received:
    246
    Location:
    Jersey
    Country:
    United Kingdom
    Is it possibly a contacter very close to the meter? I had one in my CU as it was dual tariff, and also a BX2000 unit for the hot water. Both made quite a noise when they switched in or out
     
  9. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    What I wrote is what I meant, but there are 2 ways of reading it! Perhaps I should have written "using the DW and dryer only at night". We have little else in the house that is high electrical power, except the WM and kettle.
     
  10. Sponsored Links
  11. kai

    kai

    I had economy seven in a previous home, it sure did make a loud clunk, as the heavy duty contactors switched in and out accordingly.
     
  12. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    Mine (dual-rate meter) was totally silent.
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    46,696
    Thanks Received:
    3,013
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Fair enough - we obviously read it in those two different ways!
    Again, fair enough - but I would be very envious if your total electricity usage were only about 3 times that attributable to (presumably, at most, for an hour or two per day) of a DW and dryer!

    Kind Regards, John
     
  14. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    46,696
    Thanks Received:
    3,013
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    That sounds very similar to what happens here - but, in my case, it really has to be the timeswitch making the noise. There's no contactor, the output from the timeswitch just being a 'signal' line to the electronic dual-tariff meter.

    Kind Regards, John
     
  15. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    Low energy lighting almost throughout, a couple of fairly modern TVs, fridge, freezer, my PC...
    The DW and dryer both have eco modes, but can run for 4 hours or so.
     
  16. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    My dual-tariff meter did not have a separate timeswitch.
     
  17. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    587
    Location:
    Warwickshire
    Country:
    United Kingdom
    The only dual tariff digital meters I've lived with have been totally silent - AIUI the new meters that only supply one board don't really need to any actual switching, they just switch over from counting rate 1 and begin to count rate 2.

    I would get rid of the E7 asap, I've gotten rid of it everywhere I've lived that's had it (no storage heaters etc). If I recall, it works out 5p a unit more expensive in the day, and about 3 or 4p a unit cheaper at night to run E7 (Different suppliers may vary)
     