- Joined
- 1 Sep 2006
- Messages
- 676
- Reaction score
- 3
- Country
ChrisR said:They've been adding a bit to the ACS recently, to emphasize that Meter working pressure can be 19mbar, and at full flow (say 60kW) the meter+governor can drop a further 4mbar.
Add your 1mbar pipe drop, and you get 14mbar as "acceptable" at the boiler.
I believe the words are Pressure Absorbtion or did it change
Bear in mind Chris that a U6 will flow 6 metres cubed/hour. Even a 42kw Worc doesnt use that much gas so the drop across the meter shouldnt be that great, but you are right in what you are saying.
Stan