    Hi All

    I have a problem in that the central heating system even when turned to hot water only produces just luke warm water for the shower even if it is turned for a few hours!

    The system is Valiant Boiler conventional system and is a sealed system. What is unusual is that downstairs radiators remain cold when hot water is called for but upstairs radiators warm up.

    Am i right in thinking this could be a 3 port valve problem? I know that the port is 22mm Honeywell 3 port Valve only replaced 3 years ago!

    Any help would be greatly appreciated.

    Many Thanks

    Caesar
     
  2. Sponsored Links
  3. easyflow

    easyflow

    Joined:
    12 Jan 2008
    Messages:
    472
    Thanks Received:
    60
    Country:
    United Kingdom
    You are right to think its a 3 port valve, the fact its only 3 yrs old don,t matter, check the wiring is in order.
    Should be a lever on the valve that enables you to open it manually to get hot water if it packs up.
     
    • Like Like x 1
  4. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,246
    Thanks Received:
    1,788
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    3 port valves are open to the hot water cylinder by default, so if the radiators are heating then either the valve has physically jammed in the heating position, or there is a wiring problem.

    With HW only selected, the valve should not receive any power on either grey or white wires.
     
  5. Caesar

    Caesar

    Joined:
    8 Nov 2006
    Messages:
    288
    Thanks Received:
    7
    Location:
    London
    Country:
    United Kingdom
    Hi Easyflow / Flameport

    Thanks for your replies and pointing me in the right direction. Could the synchron motor be at fault? If so any way to test the 3 Port Valve and if so what is the procedure etc?

    Many Thanks
     
  6. pete50

    pete50

    Joined:
    19 Mar 2017
    Messages:
    785
    Thanks Received:
    155
    Country:
    United Kingdom
    My same symptoms were caused by an air lock in the coil. I changed the complete motorised valve and it was still the same. I then fitted a bleeder to the coil feed pipe and BINGO hot water again. I don't know whether your actuator has an indicator but if it has and its pointing to water when you only have the hot water on then if you are not getting hot water it can only be the valve or an air lock. Mine was an airlock.
     
  7. Sponsored Links
  8. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,246
    Thanks Received:
    1,788
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    No. If it was, the valve would be permanently at hot water only and the heating would never work.

    Test voltage at the wiring centre on the actuator grey wire and the white wire. Voltages should be:
    HW only = grey 0v, white 0v
    Heating & HW = grey 0V, white 240V
    Heating only = grey 240V, white 240V.
    Nothing selected = grey 240V, white 0v
    If any of those are wrong, there is a wiring problem or the programmer/timer/other is defective.

    If those are correct, remove the actuator from the valve, and see if the spindle can be turned by hand - it should move easily. If not, the valve has seized.
     
    • Thanks Thanks x 1
  9. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,091
    Thanks Received:
    1,393
    Location:
    North
    Country:
    United Kingdom
    Could it not fail in ch then? I was led to believe that it stays in last known setting?
     
  10. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,246
    Thanks Received:
    1,788
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Grey only will hold the valve at CH only if it was already there.
    Without any power, the default is always HW only, and if HW is requested, grey is disconnected.
     
    • Thanks Thanks x 1
  11. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,091
    Thanks Received:
    1,393
    Location:
    North
    Country:
    United Kingdom
    So basically, if the grey loses the 230vac, then it springs back?
     
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page