Main 24 HE Combi Boiler strange behaviour

Joined
9 Apr 2022
Messages
9
Reaction score
1
Country
United Kingdom
Hi
I'm looking for help with strange behaviour from a Main 24 HE Combi Boiler.

Symptoms are when turning the boiler on regardless of either heat & DHW or just DWH are after 5 secs the lights show:
Burner light is off
Flame failure light is flashing slowly
Power on is on

The boiler won't fire.

However, if a call for heat or DHW is made at the same time as turning on the boiler it fires up and works until the call for heat is stopped and then the above lights show again and the boiler will not fire.

I have had a Baxi engineer look at the boiler but he couldn't figure out the issue, he changed the pcb, diverter valve and pressure differential assembly.

Thanks in advance for any thoughts on this.




Link removed
 
Sponsored Links

CBW

Joined
26 Sep 2019
Messages
14,883
Reaction score
4,634
Location
North
Country
United Kingdom
If it’s the same as this (photo) then suspect the pressure or circulating pump.

@gas112 or @ianmcd might be able to confirm this.
 

Attachments

  • B756702C-9A29-4B37-AEB3-D8F098325AB3.jpeg
    B756702C-9A29-4B37-AEB3-D8F098325AB3.jpeg
    40.1 KB · Views: 50
Joined
9 Apr 2022
Messages
9
Reaction score
1
Country
United Kingdom
Hi Chris,
Thanks for your reply, the system pressure is good and I suggested a pump issue to the Baxi engineer after looking at the same troubleshooting page as you. He dismissed it as the heating works if there is a call for heat when the boiler is first switched on.
Cheers
Bruce
 

CBW

Joined
26 Sep 2019
Messages
14,883
Reaction score
4,634
Location
North
Country
United Kingdom
However, the call for heat then extinguishes and you get loss of flame, after 5 seconds?
 
Sponsored Links

CBW

Joined
26 Sep 2019
Messages
14,883
Reaction score
4,634
Location
North
Country
United Kingdom
So, how do you reset it, or do you not? It might just be a case if fixing that then?
 
Joined
9 Apr 2022
Messages
9
Reaction score
1
Country
United Kingdom
ok let me try again with this link video
I turn the boiler off and on and provided there is a call for heat it will work until that call stops
 

CBW

Joined
26 Sep 2019
Messages
14,883
Reaction score
4,634
Location
North
Country
United Kingdom
That is odd behaviour. I’m surprised with the Baxi engineer though. I would be tempted to look at the flame signalling (rectification). This isn’t a diy job though.
 
Joined
27 Oct 2009
Messages
26,550
Reaction score
10,882
Country
United Kingdom
very strange one would need to be in it to see what the hell its doing , possible loom fault . Did he change the sensors as they can throw up strange faults on these
 
Last edited:
  • Thanks
Reactions: CBW
Joined
8 Apr 2008
Messages
10,731
Reaction score
2,712
Location
Essex
Country
United Kingdom
Disconnect the wire to the condensate trap and see if that affects what's happening.
 
Joined
15 Aug 2010
Messages
26,733
Reaction score
13,334
Location
Livingston
Country
United Kingdom
in your video to reset you are turning the control kno to O dont do this, when the flame failure light comes on, turn and hold the control knob to the "reset" position, hold in that position for about 15 seconds then release, does this make any difference ?
 
  • Thanks
Reactions: CBW