Main Earth Size
Is he using the CU earth rail as the MET? Maybe better to go for a separate MET in that instance.
Lectrician said:
No, but it aint gunna fit into a 4 wylex is it!
Oh, sorry, hadn't noticed he had a 4 way wylex CU.
Wait a minute! Who mentioned a 4 way wylex CU?? :wink:
New2Game said:
Table 54H states 10mm for 35mm or less neutral conductor if PME system
That's for main equipotential bonding conductors, not main earthing conductors.
54H is for main equipotential bonding conductors. It is not correct for the main earthing conductor. For the size of the main earthing conductor you need to consult table 54G. You should also contact your network operator as they may have additional requirements.
Bah, too slow :wink: