If we take that example we can see if it would be compliant to BS7671A calculation of Zs might be Ze + R1+R2 = Zs.
Example:
1) the R1+R2 of a lighting circuit might be 1.5 ohms (DC resistance)
2 the measured external Ze might be 0.35 ohms (impedance)
3) the Zs would be 0.35 + 1.5 = 1.85 ohms.
Adding to the above... from GN3 the reason that Ze is required to be measured is two fold:
To verify that there is an earth connection.
to verify that the Ze value is equal to or less than the value determined by the designer and used in the design calculations.
Don't forget to test polarity at the origin of the installation - those meter guys sometimes swop the live and neutral tails .... just to test you
Ze is measured using an earth fault loop impedance tester at the origin of the installation. This is a live test.....and I will assume you have the appropriate tester , nulled the test leads and it is working correctly.
Ensure that everyone in the property is made aware that the test is taking place.
Then ensure that the main switch at the Consumer Unit is open.
Remove the suppliers earth connection (to ensure that there are no parallel paths) from the Consumer Unit. Then test between the suppliers incoming live and earth connection. This is your external loop impedance Ze. (note: some testers require you to also connect to the suppliers neutral as well).
Replace the suppliers earth connection. I would normally take the Prosepctive Fault Current at this stage.
For R1+R2 (lighting as described above) ensure that there are no accessories in the circuits (lamps, dimmer switches, motors etc) and switches are closed. This is a dead test so make sure the main switch is open.
At the consumer unit provide a temporary link between the test circuit and the earth bar. (Don't forget to remove it at the end of the test)
Then using a low resistance ohmmeter measure between the line and earth at each point on the circuit - recording the highest reading, which should be the last point on the circuit. You can also test for polarity at this point by opening the switch.
Add Ze to R1+R2 to give you Zs.
Use Zs to check the max earth loop impedance for the MCB with the appropriate tables in the BRB
As stated the measured value of Zs is likely to be less than the Zs=Ze +(R1+R2) value - You can use either.
Hi not trying to be picky but as the second test should only be done on a dead circuit. Riveralt you say for the live test ZE main switch should be open you then say for the dead test main switch to be open too..
Could be a little sparky.
I think you're probably being a bit unfair to riveralt here, and I thnink I agree with what he wrote - namely that the main switch should be open for both the tests he mentioned.Hi not trying to be picky but as the second test should only be done on a dead circuit. Riveralt you say for the live test ZE main switch should be open you then say for the dead test main switch to be open too.. Could be a little sparky.