Again, everybody goes around the houses to explain something that really is quite simple.
Measuring R1 +R2 is one method of proving continuity of the circuit protective conductor within a circuit,
before energising the installation.
Measurement of R2, (also acceptable), is another method of proving CPC continuity within a circuit.
Noting the value of these measurements -
1) Shows you've actually done the tests.
2) Allows comparison with design calculations/specs in order to identify any faults before energising.
3) Gives a reference point for future testing.
After performing the R1 + R2 test the installation is plated up, all conductors terminated, sockets screwed back on, light fittings screwed up etc etc.
In other words a lot could go wrong - e.g. slightly overtightening a cpc in CU after R1 + R2 and snapping the conductor in the terminal, giving a high resistance, (if any), connection...........
So, we come to Zs.
If you wish to calculate Zs by sitting in your van and adding R1 + R2 + Ze, then so be it......but you won't find out about the snapped conductor in the CU.
My point is that assuming one has measured the (true) Ze (and found it to be acceptable) and the R1+R2, then, unless the R1+R2 is so ludicrously high that it needs to be investigated and corrected in its own right - the actual value of the Zs is of no relevance or importance.
Kind Regards, John
It is of relevance and importance because you may have had CPC continuity back during the dead tests, but that doesn't mean something hasn't gone wrong since.
Zs is 'measured' to confirm the existence of an earth fault path in an energised, fully functional installation.
I would always measure Zs because :-
1) It confirms the circuit actually has a CPC during normal operation, and that it's impedance is sufficiently low to trip the protective device under fault conditions.
2) By comparison with the 'calculated' figure and the design specs, it confirms that everything is as it should be.
And I would hate to be the person who performs all his Zs by calculation, only to find at a later date that he forgot to put the 'earthing conductor' back in the MET, after measuring Ze.
Do you therefore believe that one should always record Ze+R1+R2 and never record a directly-measured Zs
I would say yes because of what has already been said the form asks for
maximum measured Zs.
Yes, it asks for maximum
measured Zs......which is a measurement of circuit impedance - NOT R1 + R2, a dead-test measurement of resistance to confirm CPC continuity.
The question really is whether it is correct/acceptable to record a directly-measured Zs in that column, given that, as we are both agreed, that should not be used to determine whether the disconnection requirements are satisfied.
Kind Regards, John
Disconnection times are determined, and indeed, satisfied at the 'Design' stage.
Testing is done to confirm that the installation complies with the design.
It will already have been determined as to whether a particular circuit's Zs will be low enough to trip the protective device, with testing you are confirming this............which is why I say MEASURING Zs is very important - to confirm that there actually is an 'Earth Fault Path', regardless of parallel paths etc etc..............any decent tester knows what to look for in these measurements and when comparing the figures.