Guys,
I've just finished installing 4 heatlamps in a smoking shed at a pub near where I live, they are controlled by 2 Danlers EXTLSW 16A(Exterior time lag switch) they work fine for about 4 hours then start tripping the breakers.
The lamps are 1200w each, wired in 4mm on two circuits, each cicuit has 2 lamps on, controlled by the time delay switch and each cicuit is on a 16a breaker. The load on each circuit is not even 9 amps.....the time switches can handle and switch any heating or lighting load upto 16a each....
Why would they trip, voltage drop in the cable isn't an issue as the furthest lamp is only 8 metres from the fuseboard.....and 4mm cable is more than. adequate for a sustained load of 2.4 kw.....
I've been a sparkie for twenty years and this is doing my head in....first time I've ever had anything to do with heat lamps.....and the way it's going it'll be the last !!
I've just finished installing 4 heatlamps in a smoking shed at a pub near where I live, they are controlled by 2 Danlers EXTLSW 16A(Exterior time lag switch) they work fine for about 4 hours then start tripping the breakers.
The lamps are 1200w each, wired in 4mm on two circuits, each cicuit has 2 lamps on, controlled by the time delay switch and each cicuit is on a 16a breaker. The load on each circuit is not even 9 amps.....the time switches can handle and switch any heating or lighting load upto 16a each....
Why would they trip, voltage drop in the cable isn't an issue as the furthest lamp is only 8 metres from the fuseboard.....and 4mm cable is more than. adequate for a sustained load of 2.4 kw.....
I've been a sparkie for twenty years and this is doing my head in....first time I've ever had anything to do with heat lamps.....and the way it's going it'll be the last !!