Hello chaps,

We've finally moved into our new house last week, and I need a bit of advice please on the installation of a NEST Protect smoke/CO2 alarm in my garage.

I have 2 incoming power circuits into my rather long garage:

1. One for lights at the front of the garage, taken from the 1st floor circuit using 2-plate method (Power at the switch);
2. The other circuit directly coming from the CU that powers the garage sockets and is then split off mid-way into an FCU for lights at the back the garage. The FCU acts like a light switch.

I need to install the NEST somewhere in the middle.

I can cut into the 2.5mm cable between sockets and take a junction from there which will use a lot less cable, or I can take a feed from the switch but will use more cable.

Would one be better than the other?

If I took a permanent live and neutral from the 2.5mm power cable and used a 1.5mm cable for the NEST, would I need to use an FCU?

Thank you.
 
Sponsored Links
We've finally moved into our new house last week, and I need a bit of advice please on the installation of a NEST Protect smoke/CO2 alarm in my garage.
Presume you mean CO but why? Is the boiler in the garage?

Would one be better than the other?
No.

If I took a permanent live and neutral from the 2.5mm power cable and used a 1.5mm cable
1mm² will be hugely oversized; no need for another 50%.

for the NEST, would I need to use an FCU?
A switch will be handy so may as well.
 
Presume you mean CO but why? Is the boiler in the garage?
Ah, yes! You presume correctly - CO... Sorry...

Boiler is in the kitchen, not in the garage. The reason I went for another NEST is that I already have two installed in the house. And the reason why I need to install a smoke alarm in the garage is because I will have a stack IT servers running 24/7, as well as my LiFEPO4 batteries once my solar installation is finished.

1mm² will be hugely oversized; no need for another 50%.
Great, even cheaper!

A switch will be handy so may as well.
I'll add one just in case and pop a 3A fuse in there.

Awesome, thanks for the advice.
 
So my plan of action is this:

Between two of the sockets, I'll safely cut into the 2.5mm² cable. I'll attach both legs of the cable into Wago 3-terminal blocks and add a 3rd cable for the new FCU. I'll take the load for the NEST using 1mm² cable from the FCU, and hopefully that'll be that...

Now, the NEST is double-insulated, so there's no available terminal on the NEST for a CPC, so I'm a bit stumped as to what to do. There'll obviously be a connection for the CPC within the FCU, so am I best to just attached a Wago to the other end to safely terminate it? From the short length between the FCU and the NEST, I guess I could attempt to pull out the bare CPC conductor, would this be advisable?

Once all connections are teminated correctly, I'll add the Wago joins into a Wago box and zip-tie it all up to be maintenance free.

Please let me know if I'm incorrect, or have overlooked anything.

Many thanks.
 
Sponsored Links
I've taken a pic (please excuse the mess) and added some crude arrows and text boxes to explain where the two sockets are and where I intend to make the cut for the new junction.

garage.jpg
 
Thinking about it, instead of cutting where I originally intended to cut, can I take a feed from Socket 1 directly into a new FCU? If I'm not mistaken, this would be classed a spur off of Socket 1 - correct?
 
Thinking about it, instead of cutting where I originally intended to cut, can I take a feed from Socket 1 directly into a new FCU? If I'm not mistaken, this would be classed a spur off of Socket 1 - correct?
Yes, that is what I had in mind.

As it turns out the socket is not nearer than the junction box would be but that doesn't matter; it is better not to have JBs if they can be avoided.
 
Awesome, thanks for your help; I'll get everything I need and make a start on it this weekend.

Just one more question, which might not even matter, but i'll ask anyway just in case:

Should the FCU be placed close to the NEST, or can it be placed it nearer to the socket?
 