    In the attached photos you can see the wiring and wiring diagram of the receiver I am looking to replace with my Nest Thermostat E Heatlink.

    My question is around the Common connection. As you can see I have a jumper from L to COM. Am I correct to believe that I should use L (brown wire) as the wire for the COM connection on the Heatlink, alongside the green/yellow for the NO? I would then cap off the N as this is not required.

    Thanks
     

    Attached Files:

  2. Sponsored Links
  3. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,568
    Thanks Received:
    1,512
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    The terminals are marked the same on both devices. So:

    The brown wire is the Live and goes to Nest-e terminal 'C' [COM]

    The green / yellow wire is the Switched Live and goes to Nest-e terminal 'NO'

    It's bad practice to use green/yellow wire for a live connection, as a minimum it should have a brown sleeve over it to indicate this.

    No other connections at the Nest-e are required. The blue neutral wire should be insulated / isolated safely and tucked out of the way.
     
  4. jimbo1982

    jimbo1982

    Joined:
    22 Sep 2006
    Messages:
    4
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Thank you for confirming. I did think that about the wire colours. Will do as you suggest and use a sleeve.
     