Nest Thermostat E Heatlink installation (replacing Strom receiver for Valliant ecoPure Plus)

Joined
22 Sep 2006
Messages
4
Reaction score
0
Location
Hertfordshire
Country
United Kingdom
In the attached photos you can see the wiring and wiring diagram of the receiver I am looking to replace with my Nest Thermostat E Heatlink.

My question is around the Common connection. As you can see I have a jumper from L to COM. Am I correct to believe that I should use L (brown wire) as the wire for the COM connection on the Heatlink, alongside the green/yellow for the NO? I would then cap off the N as this is not required.

Thanks
 

Attachments

  • Wire Map.jpg
    Wire Map.jpg
    233.8 KB · Views: 175
  • Wiring.jpg
    Wiring.jpg
    261.4 KB · Views: 169
Sponsored Links
The terminals are marked the same on both devices. So:

The brown wire is the Live and goes to Nest-e terminal 'C' [COM]

The green / yellow wire is the Switched Live and goes to Nest-e terminal 'NO'

It's bad practice to use green/yellow wire for a live connection, as a minimum it should have a brown sleeve over it to indicate this.

No other connections at the Nest-e are required. The blue neutral wire should be insulated / isolated safely and tucked out of the way.
 
Thank you for confirming. I did think that about the wire colours. Will do as you suggest and use a sleeve.
 