How does lowering the MCB size make a ring with a faulty CPC any safer? A 6amp current is going to kill you, just as a 32amp one will.
I've been struggling to understand, too, but I think I may have worked out what he's trying to say, particularly since he has now said "Obviously you test the circuit to prove that each point has a cpc present."
If there is a CPC present at all sockets, but the CPC ring is broken, the Zs may have become too high to achieve required disconnection times with the MCB in question. Reducing the MCB size ('temporarily') would improve, maybe rectify, that situation.
However, I think most of us would agree that if a break in the CPC ring is detected, it should be located and rectified, rather than adopting some measure to make the installation 'safer' in the presence of that fault. I suppose the latter might be justified (and perhaps even laudable) as a very short-term measure pending rectification of the fault, but I'm not sure I would be comfortable with even that. People should really not be using a circuit with a btoken CPC ring!
Kind Regards, John