Any way, onto the question, just wondering whether I'm going to require a seperate earth cable when using 2 core SWA cable? For reference, I'm going to be powering 3 x outdoor lights in the garden, a pump for a water feature and a small hot tub. I've been informed that you can use the steel wire as an earth but I've read that it is not recommended and could make the surrounding area live if a malfunction occurs. Any information would be much appreciated as I'd rather avoid this for obvious reasons!
The armour can be used as the only CPC / earth in most situations.
If a separate CPC was required, it should be part of the same cable, not a separate item.
The armour must be connected to earth in all cases, although not necessarily at both ends of the cable.
As this is supplying a hot tub, exporting the earth from the main building will be inappropriate, and therefore a 2 core cable would be used.
The size depends on the load and length of the cable.
If you really want to save money, get rid of the hot tub. It will cost thousands of pounds both to install and operate.
Obtaining cable for a few pence less per meter will save nothing.