hi all , I was hoping for some advice please . I recently moved into a bungalow with a 2008 ecotec plus 418 boiler . The system was using a mixture of the old underfloor microbore pipe and two rads supplied with 15mm . We never tested the boiler before we started work as we were told that one rad didn't work so we decided to replumb with new rads and the usual 22mm and 15mm pipe dropped down from the loft . When I say we I mean I used an experienced plumber . There are 6 rads in total 4 are new 1 original in the living room and one that was second hand that I had that I thought would be fine in the front bedroom. Anyway to the issue , basically the house just doesn't warm up the rads don't get proper hot only getting warm , I can force extra heat into each one by turning others off which suggests that no individual rads are blocked . The boiler cuts in rises the flow temp to 70 degrees as set then it seems to sit there for ages with the temp only ever getting to about 50 degrees at the boiler which equates to Luke warm rads and 13degrees house temperature at best . A boiler engineer suggested a power flush but I can't understand what good it would do as 95 percent of the pipe work is brand new and all but one rads gave been changed. He suggested that the boiler may be dirty but I'm confused because the water soon reaches 70 degrees momentarily and the flow pipe is too hot to hold. Can a pump become weak ? It's a grundfos 15/50 . The boiler has been down rated to 15 kw . I've tried it at different settings but it made no difference . The diverter valve clicks over and appears to work and I can feel the water switch direction when I switch to and from heating and hot water . It's on a y plan by the way . Any ideas would be greatly recieved I'm all ears . Cold ears !