I have recently fitted a Main system 28 HE boiler, to replace my ageing standard b/f boiler. I removed the old ch pump and wiring, as the new boiler has its own pump. I have a Drayton 3 way valve for CH/HW/both, which was new about two years ago.
When the CH is on it is fine...brilliant in fact. When HW comes on or is switched on, the pump stays on (run by the permanent live) but the voltage at the boiler is reduced to 50volts for some reason. When on CH the voltage is 240v. I have changed nothing else apart from removing the frost stat at old boiler and using the perm live for the pump overrun. The programmer is an ACL Lifestyle (Appliance Components Ltd, taken over by Drayton). I also have an ACL thermostat, circa 20years old. There is also a thermostat control to the HW boiler.
Can anyone please advise why I am only receiving 50v when on HW.
When the CH is on it is fine...brilliant in fact. When HW comes on or is switched on, the pump stays on (run by the permanent live) but the voltage at the boiler is reduced to 50volts for some reason. When on CH the voltage is 240v. I have changed nothing else apart from removing the frost stat at old boiler and using the perm live for the pump overrun. The programmer is an ACL Lifestyle (Appliance Components Ltd, taken over by Drayton). I also have an ACL thermostat, circa 20years old. There is also a thermostat control to the HW boiler.