Odd boiler pressure issue

Discussion in 'Plumbing and Central Heating' started by Ali Ahmed, 25 Jan 2021.

  1. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    I have a 2yr old Ideal Logic C35 boiler which is losing pressure 5 to 6 times a day. To diagnose whether it was the boiler or system, I done the following:
    1 At 1am when the boiler hadn't been used for over 2hrs, I put the pressure upto 2 bars.
    2 I isolated the boiler by turning the CH flow and return pipes and cold water pipe.
    3 Switched the boiler off at mains.
    4 Put a bag/bowl aroud the prv and condense pipe to collect ang water.
    In the morning the boiler pressure dropped to zero but absolutely no water from either pipes. A gas safe engineer who was advising me over the phone said its really srrange and there was nothing he could do. I contacted Ideal Logic and they said it was strange that no water is leaking. The advised to book their engineer for a fixed price repair of £295.00 whatever the fault. Before I take the plunge in these hard times, does anyone have any ideas as to what the problem might be?
     
    Last edited: 25 Jan 2021
  2. Sponsored Links
  3. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    6,190
    Thanks Received:
    1,619
    Location:
    North
    Country:
    United Kingdom
    If you isolated the boiler, didn’t use it at all overnight and it dropped, possibly leaking down the condense pipe, best leave it to Ideal for the fpr.
     
  4. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    I put a bowl around the condense pipe and the was no water leak
     
  5. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    6,190
    Thanks Received:
    1,619
    Location:
    North
    Country:
    United Kingdom
    Well it’s going somewhere
     
  6. MeldrewsMate

    MeldrewsMate

    Joined:
    27 Jan 2010
    Messages:
    955
    Thanks Received:
    235
    Location:
    Buckinghamshire, Darn Sarf
    Country:
    United Kingdom
    Hmmm. How did you pit up the pressure if the boiler was isolated?
    And what was the boiler temperature when you switched it off? Hot? Cold?
    Did you also isolate the cold mains water inlet to this combi boiler?

    Please remove the ambiguities and post clearly what you did, and in what order.
     
    • Like Like x 1
  7. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
     
  8. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    5,634
    Thanks Received:
    1,146
    Country:
    United Kingdom
    What exactly did you do to " isolate" the boiler ?
    I suspect you have not isolated the boiler from the flow and return pipework ,and you have a leak on your system.
     
  9. MeldrewsMate

    MeldrewsMate

    Joined:
    27 Jan 2010
    Messages:
    955
    Thanks Received:
    235
    Location:
    Buckinghamshire, Darn Sarf
    Country:
    United Kingdom
    And did anyone use or try to use any hot tap during this test period?
     
  10. Sponsored Links
  11. MeldrewsMate

    MeldrewsMate

    Joined:
    27 Jan 2010
    Messages:
    955
    Thanks Received:
    235
    Location:
    Buckinghamshire, Darn Sarf
    Country:
    United Kingdom
    Suggest you repeat the test tonight...

    1. Start with a cold boiler.
    2. Top-up to 2 bar.
    3. Isolate ONLY the heating flowand return pipework.
    4. Switch off the boiler.
    5. Review in the morning
     
    • Like Like x 1
  12. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    No, not until 7.30am when I swithed the boiler back on.
     
  13. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    The gas engineer told me which pipes to turn off. They are coloured so its easy to identify.
     
  14. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    5,634
    Thanks Received:
    1,146
    Country:
    United Kingdom
    Boiler isolation valves are notorious for not fully closing. You have a leak on the system side.
    Do you have any of your central heating pipes either buried in concrete ,or under flooring anywhere ?
     
  15. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks, will do. Message back in the morning.
     
    • Like Like x 1
  16. Ali Ahmed

    Ali Ahmed

    Joined:
    21 Nov 2017
    Messages:
    52
    Thanks Received:
    0
    Country:
    United Kingdom
    Yeah, most of the pipework is buried under floor or walls.
     
  17. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    5,634
    Thanks Received:
    1,146
    Country:
    United Kingdom
    I assumed so.
     