I hate cavity wiring at the best of times, but I've been out tonight to see a whole house using it, it looks like it may have gone in as the walls went up, Bricklayer Sparks?
Well, all was well until the current owners decided to get environmentally consious and decided to call a contractor with a tanker full of fast-foam to insulate their cavities. Got a call today from the confused resident regarding a few dead sockets on the downstairs ring (fuses checked etc).
Turned out this is quite a heavily loaded ring final and the extra heat genereated by the cable in the walls has caused them to pop out of the terminals, which I have fixed for them, tested, IR has fallen to below acceptable levels. I told them there and then that its re-wire time, no other option and if it isn't done then they need to hope they've got a direct line to the fire station.
Not interested, even when advised to get a few quotes from local competant registered sparks, said they didn't think it was as big of a risk as I said it was and didn't want the distruption of a rewire (expense not mentioned).
Now we work in a regulated (so-so) industry like the gas boys, why can't we stick condemed stickers on CU's?
I'm worred about this now, they've got 3 young daughters, should I be contacting the REC/DNO to explain the situation and get them to cut supply to the property until work is carried out?
Well, all was well until the current owners decided to get environmentally consious and decided to call a contractor with a tanker full of fast-foam to insulate their cavities. Got a call today from the confused resident regarding a few dead sockets on the downstairs ring (fuses checked etc).
Turned out this is quite a heavily loaded ring final and the extra heat genereated by the cable in the walls has caused them to pop out of the terminals, which I have fixed for them, tested, IR has fallen to below acceptable levels. I told them there and then that its re-wire time, no other option and if it isn't done then they need to hope they've got a direct line to the fire station.
Not interested, even when advised to get a few quotes from local competant registered sparks, said they didn't think it was as big of a risk as I said it was and didn't want the distruption of a rewire (expense not mentioned).
Now we work in a regulated (so-so) industry like the gas boys, why can't we stick condemed stickers on CU's?
I'm worred about this now, they've got 3 young daughters, should I be contacting the REC/DNO to explain the situation and get them to cut supply to the property until work is carried out?