old reg new reg

Joined
8 Dec 2009
Messages
339
Reaction score
11
Location
Ayrshire
Country
United Kingdom
Hi
Reg 314.1and 314.2.with 701.411.3.3 from the 17th can any one point me in the direction of the 16th ed version Iam sure the rcd as main switch is in there as well as seperation of circuits one, the bathroom rcd requirements are there to but I need the the old regs verbatum to settle a issue for a customer and I have given my 16th ed a loan of to a mate
Mac
 
Sponsored Links
Sponsored Links
Yes I know its a bit like a crossword clue no matter I can get a copy later today and look it up if I understand what it is I want that is
Mac
 
Page 33 of the 16th sorry guys needed a quick answer for a report
Cheers
Mac
 
Regulation 314-01-01 in BS7671:2001 (Amd 1 and 2) states
"Every installation shall be divided into circuits as necessary to:
(i) avoid danger and minimize inconvenience in the event of a fault, and
(ii) facilitate safe operation, inspection, testing and maintenance."
A single main RCD would not satisfy this.
Certain items of fixed current using equipment when installed in Zone 1 of a bathroom needed RCD protection, basically if it wasn't a water heater, a shower pump or SELV current using equipment then it needed to be on a 30mA RCD. Standard rules such as the items must be suitable for the zone also stand. (reg 609-09-02).
Also non fixed current using equipment installed in zone 3 should be on a 30mA RCD (609-09-03)
Also see: http://rapidshare.com/files/104429090/Pocket_Guide_1.pdf
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top