I can't see anything untoward from the wiring centre , not that it gives absolute clarity. However ,if the system worked last winter ,and nothing has been done at the wiring centre since ,I would assume the problem is the controls or the 3 port valve itself.
Testing at the wiring centre for voltages present at various terminals , in conjunction with programmer /cylinder stat and central heating stats status would be required to establish exactly where the problem is.
Can you confirm the following...
1. The cylinder stat has been checked ,as per your task for today.
2. when the central heating stat is turning the boiler on/ off ,what are the programmer settings whilst you manually have the 3 port latched ?
2. when the central heating stat is turning the boiler on/ off ,what are the programmer settings whilst you manually have the 3 port latched ?
I am getting a bit confused. If the programmer is set to have central heating on ,and DHW ( domestic hot water) Off. And the 3 port set to its Auto position ( not influenced by you manually) your boiler does not fire up at all ,is that basically your problem ?
Agreed though it does give me information on the connections to the boiler. This helps me understand that the wiring may not be properly done but depends on what the timer needs too.. I've not yet looked for that documentationInstallation instructions are here see page 36, however likely you would need to removed sealed covers, so not really some thing you should be touching.
Pinout, the connections to the boiler based on it's terminals etc. Pinout is more of an electronics term showing what each pin on a chip or system board is for. I just used the term for the boiler for simplicity.What do you mean by .." I don't know the pin out of the boiler" ???
With programmer set for central heating ON and DHW OFF. And the central heating thermostat calling for heat ,there should be 240 v measured between earth terminal and the terminal that holds the grey wire from the 3 port and there should also be 240v measured between earth terminal and the terminal that holds the white wire from the 3 port.
Are you competent to measure these safely on a live circuit ?
Drayton MA1 actuators are the spawn of the devil. Ifit all worked last year and you have made no wiring changes and checked the thermostat operations, both cylinder and room, then there can only be one culprit. If you shop around, you may find it is cheaper to buy a complete valve rather than just a head, then just use the actuator.