One pipe system

Discussion in 'Plumbing and Central Heating' started by tomsim, 10 Jan 2021.

  1. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    I have friend who has just bought a house who wanted a rad. Removing for the plasterer. Upon looking at the system via lifting a board it turns out it's a one pipe system. Can these occasionally work ok? I the past I have ripped out and repiped. But all the radiators where buggerd in that house.
     
  2. Sponsored Links
  3. Nige F

    Nige F

    Joined:
    28 Jun 2005
    Messages:
    21,055
    Thanks Received:
    1,717
    Country:
    United Kingdom
    Occasionally, yes - if it was sized and installed correctly back in the middle ages ;)
     
    • Thanks Thanks x 1
  4. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    I think the house is the 70s. If it was my house I'd rip out and start again. Is a new boiler. But don't think he'll want to go to this. Every thing appears to be working OK. There's a pipe going around so if you turn one rad off it won't shut the hole system down. His on about swapping the bathroom rad. For a towel rad. This should work ok on a one pipe system?
     
  5. Nige F

    Nige F

    Joined:
    28 Jun 2005
    Messages:
    21,055
    Thanks Received:
    1,717
    Country:
    United Kingdom
    So leaving that pipe in place and just connecting a towel rad to the old rad flow and return - should be fine
     
    • Thanks Thanks x 1
  6. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    It's a sealed system off a combi are they no more prone to air locks when refilling than a two pipe system. Usually OK on a sealed system.
     
  7. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    Any advice on this one? A new combi boiler was installed on the system 2 years ago. Should it really be converted or just leave alone? Thanks
     
  8. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,651
    Thanks Received:
    1,064
    Country:
    United Kingdom
    I know what I would do !! For every 10 one pipe systems I have worked on unless large bore commercial, maybe one would give reasonable heating. Customers are amazed at system performance after a re pipe!!
     
  9. cross thread

    cross thread

    Joined:
    8 Sep 2005
    Messages:
    1,537
    Thanks Received:
    237
    Location:
    worlds end
    Country:
    United Kingdom
    Thing is they will eventually want rads and valves that are not suitable for one pipe
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. AdrianUK

    AdrianUK

    Joined:
    22 Sep 2009
    Messages:
    569
    Thanks Received:
    87
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Don't forget there has to be a fair length of pipe between the flow & return connections for a radiator with a one pipe system.

    If this is too short, too much water takes the short route & the radiator doesn't get hot.... I found this the hard way :(
     
  12. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    It flows in one side it thenI think you call it bypass pipe that carries on to and picks up the return from the rad. And to the rest of the system. So you can turn the rad off without shutting down the system. Do you mean a fair length of pipe as in the rad. Needs to be a decent size?
     
  13. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    Are towel radiators suitable for a one pipe system?
     
  14. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    And do the valves need to be specialist?
     
  15. cross thread

    cross thread

    Joined:
    8 Sep 2005
    Messages:
    1,537
    Thanks Received:
    237
    Location:
    worlds end
    Country:
    United Kingdom
    There are valve and rads more suitable tend to be less restricted
     
  16. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    Would a towel rad. Work the as its got large water ways?
     
  17. tomsim

    tomsim

    Joined:
    4 Apr 2010
    Messages:
    450
    Thanks Received:
    1
    Location:
    Humberside
    Country:
    United Kingdom
    Am I also correct in saying that it's unadvisable to use tight elbows on the system. The rest of the system has machine bends
     