Optimum gas boiler temperature?

Not often I disagree with Ianmcd but there will be an efficiency increase if you change from standard to condensing appliances; how much depends on the boiler. It's fashionable to think of continued running at low temperatures as cheaper also than cycling but too much depends on how the house loses heat and if there is an anti-cycle delay on the boiler, what it is set for and the type of heat exchanger. It's pointless measuring the condensate from that boiler to determine how it is condensing as the flue and exchanger condensate exit together I believe. To give any reference to how efficient the exchanger is you need the condensate from the exchanger alone unless you subscribe to the belief that condensate in the flue warms the incoming combustion air to any significant extent.
 
It would never be touched. The shower is just to the other side of it. The wall is tiled that side. I must just check no water is seeping through

Best get it checked anyway.

asbestos cement board.JPG
 
To give any reference to how efficient the exchanger is you need the condensate from the exchanger alone unless you subscribe to the belief that condensate in the flue warms the incoming combustion air to any significant extent.
I wouldn't say it warms it significantly so i don't subscribe to that view either.
However assuming a concentric flue, where does the latent heat of any condensation in the flue go?

I do agree measuring condensate volume doesn't tell the whole story, if the boiler isn't condensing at all the efficiency can still vary, but once it's in condensing mode it would be ok.
Even in non condensing mode it would be a bit better than an old school boiler just due to the lower flue gas temperature, but i think that's common knowledge around here anyway.
 
I wouldn't say it warms it significantly so i don't subscribe to that view either.
However assuming a concentric flue, where does the latent heat of any condensation in the flue go?

I do agree measuring condensate volume doesn't tell the whole story, if the boiler isn't condensing at all the efficiency can still vary, but once it's in condensing mode it would be ok.
Even in non condensing mode it would be a bit better than an old school boiler just due to the lower flue gas temperature, but i think that's common knowledge around here anyway.

Look at the plume at the terminal, the latent heat goes to the same place as sensible heat in the flue products, the atmosphere.
 
Look at the plume at the terminal, the latent heat goes to the same place as sensible heat in the flue products, the atmosphere.
We were talking specifically what condenses in the flue itself, i agree that when the flue gas leaves the terminal the is still a lot of condensing to happen but the condensate from that won't end up in the condensate drain, more likely end up as rain.
 
We were talking specifically what condenses in the flue itself, i agree that when the flue gas leaves the terminal the is still a lot of condensing to happen but the condensate from that won't end up in the condensate drain, more likely end up as rain.

Based on what? Hot flue gases are surrounded by cold ambient air through a thin tube. In winter the ambient air can be between -5 and 14 degrees. And still there's a plume, that shows the efficiency of the boiler then the flue in removing latent heat with is less than 10% of the potential of the fuel burned.
 
sorry, let's start again as I think we're on different pages of the book by now:):
  • my suggestions measure the condensate output to compare relative efficiency (all this assumes the flue gas leaves at 100% humidity, i.e. condensing mode)
  • you mentioned that also covers flue condensation, but only hex condensation should be taken into account (unless people believe it warms the intake air much)
  • my point if there is condensation forming in the flue, there must have been a surface cooler than the flue gas for it to form on
  • condensing water out transfers heat to the surface
  • the other side of the surface is the intake air along almost the whole length of flue
  • so almost all the condensation in the flue will return heat to the intake air
Yes I agree it won't be much heat, but in that case there won't be much condensate from the flue.
 
That wall is asbestos but prob asbestos cement as opposed to the more dangerous AIB but providing it doesn't get disturbed it's ok to leave. But it has already been drilled at some point
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top