If you have an earth rod, then likely a TT supply, not 100% as I have an earth rod and a TN-C-S supply, but a good pointer.

I have never worked out why EVs don't require a class II supply like most out door equipment, but ours is not to wonder why, and for what ever reason we need an earthed supply which will either has a local earth and far enough away from any other earthing system to be safe, or it has some device to disconnect the earth and lives, if there is a loss of PEN.

It does not really matter if some rule says not over 13 amp or not without loss of PEN protection, we have three options:-
1) Don't get an EV.
2) Pay out for loss of PEN protection.
3) Don't take any notice of the rules.
If not taking any notice of the loss of PEN protection, may as well take no notice of the bundled supply rule, RCD requirement rule, and all the rest, you have asked the question, and I have answered.

To my mine the granny charger is to allow the once in a blue moon charging of an EV, using an existing socket, to fit a socket with the whole idea of charging an EV, is something different, I have three double outside sockets, they are to power my leaf blower in the main, and other class II items, not to power an EV even if placed well for doing that job.
 
I want to cut the power from the outside EV socket but still be able to have power to my inside socket.
Add a 20A switch. No fuse required or desired, as fuses get hot when in use, and when in use for hours at a time at high load, they can get very hot indeed.

I can’t use a charger like hypervolt because my power is looped supply and I don’t want any digging
Hypervolt and most others can be set to a lower current rating internally, such as 16A.
 
To my mine the granny charger is to allow the once in a blue moon charging of an EV, using an existing socket, to fit a socket with the whole idea of charging an EV, is something different, I have three double outside sockets, they are to power my leaf blower in the main, and other class II items, not to power an EV even if placed well for doing that job.
Thank you, are you saying its not advised to use the granny charger 2 or 3 times a week? I can see where you are coming from, I have noticed the plug warm when charging.... food for thought. Thank you.
 
Add a 20A switch. No fuse required or desired, as fuses get hot when in use, and when in use for hours at a time at high load, they can get very hot indeed.


Hypervolt and most others can be set to a lower current rating internally, such as 16A.
Thank you but am I still suppose to notify my DNO if installing a Hypervolt reduced to 16A?

Are you saying use a 20a switch instead of a fused spur?

Thanks.
 
Last edited:
Back in the 1970s, the load in any street was reasonably even, the three phases were alternated house to house, so the neutral current was rather small.

But since then we have seen solar, batteries, off-peak, EV charging and a lot more, which has resulted in some very high currents in the neutral, with those high currents comes the risk of a poor connection causing the loss of the combined neutral and earth (PEN) becoming a lot higher.

Reports of broken PEN (protected earth and neutral) conductors increased from 57 in 2003 to 474 reports last year, says a IET report dated Thu 24 Nov 2022 updated 20 Jun 2026, not sure if those numbers have also been updated?

But it seems likely the numbers will rise further, so as time goes on, having earth rods becomes more important.

A single earth rod of 1.2 meters has an earth loop impedance of some where around 60Ω so with a 100 amp supply, with an earth loop impedance of 0.35Ω the 60Ω earth rod has very little effect. So what we hope is there are loads of earth rods, which is why it was called PME, the M stands for multi, but with TN-C-S there may not be that many earth rods, so if one phase ends up connected to earth the other two could be 400 volt in respect to earth, it will never likely get to that stage, and 50 volts AC to earth is considered in normal clothing to be safe, with EVs I think 75 volt is allowed, this will still give one a nasty shock, but unlikely to kill you.

What is hoped is some loss of PEN detection device will detect the problem and disconnect before anyone touches the part with the voltage.

So most outdoor equipment simply does not have an earth connection, and if not outdoors, then because all is bonded together, like the birds on the power line, you will not get a shock, so if you charge your EV in a garage, then no real problem with loss of PEN.

And with a TT supply there is no PEN to loose, so charging an EV in a garage or with a TT supply is not a problem shock wise, there may be a fire problem, but not shock.

So to sell a 13 amp socket to charge an EV in a garage or with TT supply is not a problem, but same socket with a TN-C-S supply is. Same goes for solar panels, patio heaters, and outdoor hot tubs etc. Putting an earthed grid under the patio can help, but then looking at how much fault current, to earth whole street to your patio re-bar is not really a good idea.

Basic PME should now be banned, it is no longer a safe practice, but I can't see that happening any time soon. More likely the way the Welsh government was going under labour, was to have a red flag waved in front of cars again.
 