Another contractor had issued a code1 on a PIR against an installation in a small commercial unit, for an overrated protective device:
"32A MCB for 2.5mm PVC/PVC cable" with the recommendation of "Either downrate to 20A or upgrade cable"
(In fact it is a 32A RCBO in a Talisman BT016 Board)
So it sounded like like it was a radial circuit and above seemed correct (Although would you say thats immediate danger and therefore code 1 ??)
I expected to have to replace the rcbo for a 16/20A, however on enquiry these were circa £260 from C.E.F !!!!)
On inspection and test the circuit in question was in fact a ring final, serving a few double sockets, with a spur connected at the consumer unit which may may have given the impression at first glance that the circuit was a radial. (but to my first glance saw the other two phase connectors at the mcb and assumed ring)
Questions are:
i) If it had been a radial would it warrant code 1 (No evidence that the circuit was heavily loaded or likely to be, in fact the opposite)
ii) How would you document the fact you disagree with original PIR ? Issue another PIR ?
"32A MCB for 2.5mm PVC/PVC cable" with the recommendation of "Either downrate to 20A or upgrade cable"
(In fact it is a 32A RCBO in a Talisman BT016 Board)
So it sounded like like it was a radial circuit and above seemed correct (Although would you say thats immediate danger and therefore code 1 ??)
I expected to have to replace the rcbo for a 16/20A, however on enquiry these were circa £260 from C.E.F !!!!)
On inspection and test the circuit in question was in fact a ring final, serving a few double sockets, with a spur connected at the consumer unit which may may have given the impression at first glance that the circuit was a radial. (but to my first glance saw the other two phase connectors at the mcb and assumed ring)
Questions are:
i) If it had been a radial would it warrant code 1 (No evidence that the circuit was heavily loaded or likely to be, in fact the opposite)
ii) How would you document the fact you disagree with original PIR ? Issue another PIR ?