I finally managed to find a spark to do a PIR on the electrics in an extension as requested by the BCO after the builder 'disappeared' before getting the work signed off.
Everything looks OK except for a couple of notes from the spark doing the testing.
1. No earth bond between sockets and back boxes.
There is one fixed lug on boxes, so they should be earthed through the fixing screw, and I believe opinions are divided on that one. It won't take much to put straps in half a dozen back boxes anyway.
2. No fire hoods on downlighters.
It's a ground floor extension with downlighters recessed into the two foot high loft space above. The insulation is cleared from around the fittings.
I thought fire hoods are only required when there are habitable rooms above.
3. No equipotential bonding in shower room.
the plumbing is all plastic so there's nothing to bond to, except where numpty builder decided to cut the plastic pipes short and put push-fit elbows inside a stud wall where nobody can get to them when they start leaking and fit 3" long copper tails to poke through the plasterboard and join back onto plastic pipe inside the room
I'm just wondering if I will have to do any remedial work to keep the BCO happy before submitting the cert. as time is getting very short. Everything should have been signed off by December.
Everything looks OK except for a couple of notes from the spark doing the testing.
1. No earth bond between sockets and back boxes.
There is one fixed lug on boxes, so they should be earthed through the fixing screw, and I believe opinions are divided on that one. It won't take much to put straps in half a dozen back boxes anyway.
2. No fire hoods on downlighters.
It's a ground floor extension with downlighters recessed into the two foot high loft space above. The insulation is cleared from around the fittings.
I thought fire hoods are only required when there are habitable rooms above.
3. No equipotential bonding in shower room.
the plumbing is all plastic so there's nothing to bond to, except where numpty builder decided to cut the plastic pipes short and put push-fit elbows inside a stud wall where nobody can get to them when they start leaking and fit 3" long copper tails to poke through the plasterboard and join back onto plastic pipe inside the room
I'm just wondering if I will have to do any remedial work to keep the BCO happy before submitting the cert. as time is getting very short. Everything should have been signed off by December.