I'm confused, which is it? Obviously we are 5 months on now.
This all needs electrically tested and the switching live out (240V) from the boiler needs to be traced around the system. It also needs checked at the wiring centre above the UFH controller. There should be a common switched live back to the boiler (blue). The UFH controller should have it's own live and shouldn't be using the live out from the boiler.
If, as per the original post, the boiler is always getting a signal then that needs to be found - either from the UFH controller or the stat.