Close both valves on the problem rad. If system is sealed / pressurised ensure pressure is 1.5 bar . Then open its bleed valve ,have a towel to hand ,let water run out until it stops running. Open the TRV and see if water starts ,and continues , to flow out . If it doesn't the TRV is faulty or the pipework to it is blocked.
If water does flow out well,close the TRV and open the lockshield and repeat the test to see if water flows.