@mrbg07546 I'm lost for words. Just read my signature. That's all there is too it.
This is reason . But not the solution.This was on page 3 and then followed eight pages of you ignoring the advice thinking it was just a case of pressing the right button to cure all.
A 627 has an integral diverter valve for use with a cylinder (a four pipe boiler to professionals). Your installer clearly has no idea! You need to start again...
Zone valves are not required
I suspect the boiler has not been set/commissioned properly.
All the pipework is needed it's the valves I don't think are needed.
The boiler/system setup. Doesn't know it needs to open that valve.
They'll have to get it to open first
Page 2... lolDitch the VR66