Potterton Profile 100e overheat trip - strange one

Joined
3 Jan 2022
Messages
2
Reaction score
0
Country
United Kingdom
Hope someone can shed some light on this...
Potterton 100e - motorised valves to hot water tank and to heating.
Over-temperature cutout trips about the same time every few days, more often if I turn the temperature on the boiler up (set about 3 now).
This has been bugging me for a while so I have temperature loggers in various places on the pipes - thermocouples on: flow; after valve to heating; after valve to tank
Heating is programmed to come on followed by the water 30 minutes later.

I can see the flow temperature cycling up and down every ~5 minutes, when the hot water program starts the boiler cycles twice then on the third time it doesn't turn off, just keeps getting hotter until it trips out with the flow temp around 92C.

After I reset the boiler it will work fine for a days or so, then do the same thing again.
It seems clear from the temperature readings that both heating and water valves are open, the issue seems related to the boiler control but seems a very specific circumstance.

Controller seems the obvious choice but possibly a sticking "gas valve"? Or the boiler temperature sensor sticking?
 
Sponsored Links
Joined
15 Nov 2005
Messages
77,089
Reaction score
4,781
Location
Crossgates, Europe
Country
Cook Islands
Have you got a system filter?

Is the boiler about 30 years old?

When was the system last cleaned to remove sludge, sediment and scale?
 

CBW

Joined
26 Sep 2019
Messages
11,564
Reaction score
3,231
Location
North
Country
United Kingdom
I don’t know why you think a sticking gas valve, but it’s more likely a failing pump or something else causing it to overheat.
 
Joined
3 Jan 2022
Messages
2
Reaction score
0
Country
United Kingdom
The boiler is 20 years old, I treat the water every couple of years and when I last took a radiator off the water was fairly clean, no sediment to speak of (though it could just be somewhere else in teh system). I don't have a filter but its on the list. The reason I wondered about something sticking is that from the tempearture sensors I can see the flow temp cycling every ~5 minutes but then it stops cycling and gets hotter and hotter over the course of just 5 minutes. I would expect a sludged up system to just run hot permanently or get hotter over a longer period.

Take a look at the flow temperature plot below
Capture.PNG


At 06:30 the hot water valve turns on and the flow temp drops but after two heat cycles it just gets hotter and hotter (>90C) as if the boiler has stopped regulating - it just stops cycling.
 
Joined
7 Jan 2010
Messages
10,783
Reaction score
1,733
Location
Dystopia, a small island too close to Europe
Country
United Kingdom
What is the temperature of the return pipe ? Does the heating come on a t 9 AM, and is there a balancing/restricting valve on the cylinder return ? Could be the hot water circuit is restricted so the return to the boiler doesn't get hot enough for the boiler to shut down, but does when the heating runs.
 
Joined
27 Oct 2009
Messages
24,258
Reaction score
8,791
Country
United Kingdom
Boiler should only get to 82 even on max
it could be
boiler stat old and out of calibration
gas valve not fully going out
pump not getting power everytime (faulty pcb /pump over run stat )
There is a switch by control panel behind bottom tray for gravity and fully pumped make sure someone has not put it to wrong setting
 
  • Thanks
Reactions: CBW

DP

Joined
10 Dec 2003
Messages
15,546
Reaction score
3,497
Location
Glasgow
Country
United Kingdom
Have you got a system filter?

Is the boiler about 30 years old?

When was the system last cleaned to remove sludge, sediment and scale?

If the system water had boulders in it, these would pass through the heat exchanger waterways without breaking in a sweat :whistle:
Boiler is from an era where sedimentation was no problem same as eating deep fried Mars bars
 
Joined
15 Nov 2005
Messages
77,089
Reaction score
4,781
Location
Crossgates, Europe
Country
Cook Islands
I used to have one, a huge amount of sludge came out when I cleaned it

and another huge amount when I converted the HW from gravity to fully pumped
 
Sponsored Links

DP

Joined
10 Dec 2003
Messages
15,546
Reaction score
3,497
Location
Glasgow
Country
United Kingdom
Hope someone can shed some light on this...
Potterton 100e - motorised valves to hot water tank and to heating.
Over-temperature cutout trips about the same time every few days, more often if I turn the temperature on the boiler up (set about 3 now).
This has been bugging me for a while so I have temperature loggers in various places on the pipes - thermocouples on: flow; after valve to heating; after valve to tank
Heating is programmed to come on followed by the water 30 minutes later.

I can see the flow temperature cycling up and down every ~5 minutes, when the hot water program starts the boiler cycles twice then on the third time it doesn't turn off, just keeps getting hotter until it trips out with the flow temp around 92C.

After I reset the boiler it will work fine for a days or so, then do the same thing again.
It seems clear from the temperature readings that both heating and water valves are open, the issue seems related to the boiler control but seems a very specific circumstance.

Controller seems the obvious choice but possibly a sticking "gas valve"? Or the boiler temperature sensor sticking?

what are you using to log the temperature
 
Joined
27 Jan 2010
Messages
1,206
Reaction score
305
Location
Buckinghamshire, Darn Sarf
Country
United Kingdom
That's a nice trace that very clearly shows the symptoms - well done. I suspect the measuring thermocouples have a lot to do with the probable error in indication of temperature, so that can be glossed-over, but it's clear to see how the flow temperature drops temporarily when the hot water load comes on at 08:30.
1. Is your circulating pump driven directly from the boiler?
2. Have you considered that the pump may be sticking or failing?
3. Is the pump set to its highest speed? If not, increase its speed and monitor the system. If the symptoms go away with a higher pump speed then suspect a pump malfunction (which could simply be debris in the impellor).
4. How far away from the boiler are the two zone valves, in pipe metres?

If the gas valve was sticking on you'd see the flame through the viewing window.
 