Hi All - Recently replaced the PCB on a Suprima 50L (to cure the lockout problem) and all was well for a week. Called back after a week as the boiler was not coming up to temperature. Boiler is firing up, getting warm and then stopping, green light flashing.
Boiler thinks that flow temp is satisfied when the boiler is only at 40 degC. So I replaced the thermistor and got the same result. Thermistor is reading about 1.1Meg Ohm at roomtemp which drops to about 500K at 40(ish) degC.
Muppet at Potterton tech support said thermistor should read 1.3 meg at 20 degC, 760K at 80 degC and 500K at 40 degC. He got very obnoxious when I asked him to check the values he had quoted me - there is no way that the NTC can be 760K at 80 deg AND be 500K at 40 deg if it starts at 1.3Meg when cold. Boiler fires fine when i take the thermistor out of the pocket but burner cuts out as soon as the themistor gets warm.
Unlikely that the new thermistor is duff. Can anyone out there tell me what the thermistor values should be at 40 deg and at 80 deg? Potterton are no help here. Perhaps the PCB is duff (it was the latest type) - hope not. Client is having cold showers.
Many thanks
pete
(corgi reg. and waiting to enter the combustion chamber...)
Many thanks
pete