Powermax 155x no central heating but h/w

Discussion in 'Plumbing and Central Heating' started by Edo7, 14 Sep 2010.

  1. Edo7

    Edo7

    Joined:
    14 Sep 2010
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi, I have turned my stat on for 1st time and whilst I get a click from the stat, the boiler does nothing not even a sound.

    Not wanting to play sob story but have a pregnant wife who is cold.

    Wondered if this known issue I can resolve?

    Hot water work. Programmer works.
     
  2. Sponsored Links
  3. Razor900

    Razor900

    Joined:
    16 Nov 2007
    Messages:
    5,753
    Thanks Received:
    2,249
    Location:
    Northamptonshire
    Country:
    United Kingdom
    The heating pumps probably seized after the summer. Clout it with a mallet or put a towel under it remove the big slotted screw and see if you can turn it with a screwdiver.
     
    • Thanks Thanks x 1
  4. Beerlover

    Beerlover

    Joined:
    7 Sep 2010
    Messages:
    1,072
    Thanks Received:
    210
    Location:
    London
    Country:
    United Kingdom
    Your heating pump has possibly only stuck (winter - we loved these!) remove the the vent cap, the silver one and spin it with a screwdriver. Some, not lots, of water will escape but be brave.

    It should be fine for a few weeks , but you will need a replacement not long afterwards. A complete drain down and a Grundfos 15/50 pump & inhibitor will fix it - when this happens.

    Cheers
     
  5. kevplumb

    kevplumb

    Joined:
    18 May 2004
    Messages:
    23,712
    Thanks Received:
    925
    Location:
    depends where i get sent
    Country:
    United Kingdom
     
    • Thanks Thanks x 1
  6. Edo7

    Edo7

    Joined:
    14 Sep 2010
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks all, i've removed the silver cap but the assuming you spin it using a screw driver it appears the head is like a crescent shape that no screw driver will fit. Almost as if it needed an Allen key but half has has come off???

    The pump is very very hot and doesn't appear to be vibrating as does the heating one.
     
  7. kevplumb

    kevplumb

    Joined:
    18 May 2004
    Messages:
    23,712
    Thanks Received:
    925
    Location:
    depends where i get sent
    Country:
    United Kingdom
    in the words of my ex wife

    it's donald ducked :cry:

    however you could try a smaller screwdriver :idea:
     
  8. Gas2Air

    Gas2Air

    Joined:
    2 Aug 2004
    Messages:
    1,559
    Thanks Received:
    165
    Country:
    United Kingdom
    This Powermax has a cold start stat that fails. Check if you have voltage to the pump before messing/whacking it.
     
    • Thanks Thanks x 2
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom