Problems Venting System

Sorry to be slow.. lots other stuff to deal with, but..
RESULT! Took a while to bleed air from system but now running nicely both CH and HW. Initially pump only using 7w on CC3 as before but after some gurgling etc it's now 40w on CC2. I guess I'll switch to PP2 once it's settled.

I'll need to fully flush X400 after a couple of weeks. I'm thinking ideally I'd fit Magna clean or similar but the boiler return isn't very accessible.

Huge thanks for your help with this.. your suggestion that pump had restricted feed even though feed tank right next to it, gave me the confidence to strip the pipework leading to it. Maybe this thread will help someone else in the future.

BTW pump reading 40w on CC2. Do you want any other readings?
 
Circulating pretty well now

CC2 (40W) is circulating 16.67LPM at a 4.9M pump head.
Based on the above, I would expect
PP2, 11.3LPM at a 2.25M pump head
PP3, 15.02LPM at a 3.98M pump head
Suggest initially change to PP3, post power.

Where was the severe pipe blockage, was it upstream (before) of the Vent??
 
Last edited:
It was in the straight section of speedfit with the 2 Tees to vent and feed. TBH I was so pleased to find any blockage I didn't check precisely, but I'm pretty sure it was at the feed T, so after the vent.
PP2 15w, PP3 28w with HW and CH on
 
OMG - RIGHT BACK WHERE I STARTED! Today X400 had been in 3 weeks, so I drained all and refilled with X100. Now it's worse than ever - can't get water to circulate at all, boiler tuns off almost immediately, pump shows 6W on CC3. I filled the entire system from the header so the feed absolutely must be clear, rads all bled. Uttelry depresssing, paid heating engineer £500, and £300+ for parts and right back where I started. Despereate for any help please.
As a reminder - I have new UPS4 pump, new autovent, and new 3 port valve. I also bled the boiler - but didnt seem to have any air in. Although when boiler does fire up it doesnt sound great... sound like air in it. Presumably when bleeding, water can run from either feed or return - so seem to me if water flows from the feed side, there could be air in the return, or vice versa.. if you see what i mean.
 
Last edited:
OK... panic over!! I had to back fill again which didnt seem to do much by way of forcing air out, but after a while and a few gurgles the pump started working properly and all good. Knowing that the wattage being used relates directly to the work its doing - ie very low watts means it's not pumping much - is incredibly useful esp with the USP4 which reads wattage directly on the display. Anyway thanks again for all the help... and I wont be draining the system again anytime soon!
 
I would never use CC3 on the UPS3 OR 4 pump to get rid of air despite what Grundfos tell you, anyhow your back in business again, good.
What pump settings are you using .now and what is the power?
 
Yes, setting to CC3 seems to be the recommended thing, but in practice turning off and the on at lower setting seemed to work better. Its on CC2 at the moment @40watts just because I know that works, but I'll test tomorrow on PP2 which should be better.
 
OK... panic over!! I had to back fill again which didnt seem to do much by way of forcing air out, but after a while and a few gurgles the pump started working properly and all good. Knowing that the wattage being used relates directly to the work its doing - ie very low watts means it's not pumping much - is incredibly useful esp with the USP4 which reads wattage directly on the display. Anyway thanks again for all the help... and I wont be draining the system again anytime soon!
Did you refill by allowing full flow through the ballcock?, it might work better if you just tied it up to let it trickle in although unlike refilling a combined cold feed and vent, I've never seen it suggested to refill your system type slowly, better off as well not to put any inhibitor in until the system is proven to be circulating properly, a rad can then be drained down by a few litres to put the inhibitor in.
 
Yes maybe slow filling is better. I also wonder if pump running might reduce pressure in the side of system with airlock and prevent auto vent working properly.
When I filled last time with x400 it vented fairly easily, so this time I was more confident and put x100 in first.. but yes, might have been safer so fill and test first. I was worried that partial drain to insert inhibitor might introduce air lock all over again.
 
I have a 15mm isol valve on the F&E cistern ballcock supply and just crack this open when refilling the combined Vent & cold feed system which are allegedly a right pain to refill due to air locking, I don't have any problems after refilling.
 
Interesting. I've also got isolating valve on FE, but didn't realise fast refill might cause issue. I'll know better next time... except that there will never, ever, be a next time!
 