Problems with DHW on vaillant turbo max

Joined
28 Jan 2008
Messages
69
Reaction score
0
Location
Birmingham
Country
United Kingdom
having problems with turbomax hot water delivery. boiler keeps cycling on and off. water is luke warm and then cold, from reading comments it points towards divertor valve but then on other occasions, the boiler wont cycle on HW but after running for a minute or so the boiler then starts to make a high pitched whining. Any ideas. Thanks.
 
Sounds like its sludged up and the hw heat exchanger is blocked.

Get the systems flushed and the hw heat exchanger changed
 
Thanks for quick reply. Do you think I also have a problem with the divertor valve or the microswitch on the valve causing the boiler to cycle on and off.
 
Not necessarily. To check for a diverter problem, wait until the CH pipes from the boiler are cool, then run a hot tap. If the CH flow pipe (leftmost) gets hot, it's "letting by".
 
Thanks lads, if flow pipe is getting warm once hot tap is running, how long will this take ( ie. will the pipe warm within seconds or minutes.)
Also how big a job to change divertor valve.
 