Protecting Electrical Cables

Joined
9 Aug 2006
Messages
3
Reaction score
0
Location
Kent
Country
United Kingdom
Hi all

I have just built a conservatory with the help from a friend in the trade.

I wanted to extent the existing downstairs ring main to add 4 double sockets in the conservatory. I have had a look on the screwfix.com website for protective channelling but they are all plastic. Is this sufficient? It doesn't seem much of a protective layer. A plasterer will cover all cables once the work is complete.

Any suggestions or comments would be gratefully received.


Best regards
Mark.
 
Thanks for your reply.

As I understand it then I guess I need it as the cables will be run against / along the wall and then covered over with plaster less than 50mm thick and will run outside the zones. I will need to at least cover the cables with an earthed metallic covering/conduit.

I can't seem to find anything other than PVC cover products though.

Maybe it's safer and easier to use armoured cable which complies with BS 5467. My only concern is it maybe a little too ridged to handle.

Does the above make sense and correct ?
 
Hmmm, reading the links posted I am now all confused.....

.... if I am running a cable vertically down a chased out wall from the ceiling to a light switch and then plastering over with 5-10mm plaster, what sort of protection do I need?
 
sam8364 said:
Hmmm, reading the links posted I am now all confused.....

.... if I am running a cable vertically down a chased out wall from the ceiling to a light switch and then plastering over with 5-10mm plaster, what sort of protection do I need?

I have re-read http://www.niceic.org.uk/downloads/C5-43.pdf and think I understand it all now.

If you have cables within 50mm of a surface and **outside** a horizontal or vertical zone then you basically need to armour the cable. If you stick within the zones you should be ok. Maybe someone could confirm that.

To clarify a point, if I run cables down from a socket along the base of the wall and then up to the next socket is this still within the zones or would I need armoured cable for that ??
 
markknell said:
If you have cables within 50mm of a surface and **outside** a horizontal or vertical zone then you basically need to protect* the cable. If you stick within the zones you should be ok. Maybe someone could confirm that.

Confirmed

To clarify a point, if I run cables down from a socket along the base of the wall and then up to the next socket is this still within the zones or would I need armoured cable for that ??

No. Look at the diagram again. There is no safe zone along the bottom of a wall. Go under the floor if you can.
 