    Hi, When the mains is removed, after a short while the panel sounds at full volume. Does anyone know how to turn this down please?
     
  2. Alarm Engineer

    Alarm Engineer

    Joined:
    24 May 2016
    Messages:
    481
    Thanks Received:
    86
    Location:
    Kent
    Country:
    United Kingdom
    Do you have access to the Enginner Menu? If so you could change the Lengh of time from a Mains Fail to the time it makes a sound in the Change timers menu or go to Volume Control menu and change Day Alarm to 2 or 0 for silent.
     
  3. swishy6

    swishy6

    Joined:
    11 Mar 2014
    Messages:
    77
    Thanks Received:
    11
    Location:
    Keighley
    Country:
    United Kingdom
    Yes but those options don't work. Change timers menu just gives option of entry/exit/sirens and I have the day alarm at 2 already.
     
  4. Alarm Engineer

    Alarm Engineer

    Joined:
    24 May 2016
    Messages:
    481
    Thanks Received:
    86
    Location:
    Kent
    Country:
    United Kingdom
    What software are you running? Early enforcers had no AC alert timer in Site options.
     
  5. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page