Quick check on cable size

My issue with using a contactor with a remote switch without also using a standard DP isolator is what happens if the contactor gets jammed on.
Is a contactor more (or much more) likely to get 'jammed on' than is a 'standard DP isolator'?

Even Main Switches in CUs have been known to get 'jammed on' (it happened to a friend of mine not long ago). This is why we test for dead', no matter what we think we have 'switched off' (and maybe also 'locked off').

Kind Regards, John
 
Sponsored Links
Many contactors are only suitable for functional switching, and are not suitable for isolation or emergency switching.

Others can be used for all three things.
 
Many contactors are only suitable for functional switching, and are not suitable for isolation or emergency switching. .... Others can be used for all three things.
As a matter of interest, what features/characteristics of the 'many' and the 'others' result in this difference?

According to Table 537.4 of BS7671, contactors to BS EN 60947-4-1 are suitable for 'all three things', whereas those to BS EN 61095 are suitable only for functional switching.

Edit: in terms of what TLC are offering, it appears that the MK ones are part of the 'many', but the Wylex ones part of the 'others'.

Kind Regards, John
 