    Running in a T&E cable for an oven only (no hob)
    This is rated as 5.9KW ..... so therefore 26A

    Quick look up for a clipped direct (method C) cable on a 3m run shows that 4mm2 is more than beefy enough at 37A

    That all correct ?
     
  2. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    8,236
    Thanks Received:
    1,513
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Yes, provided it's a 32A circuit breaker.
     
  3. RickH

    RickH

    Joined:
    10 Dec 2008
    Messages:
    281
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    Might have to re-think this a bit.
    There is a radial cct out to an MK Grid switch which is rated at 20A, this is in 4mm2 running from a 20A breaker. form the switch 4mm2 cable to a wiring connection point.
    Previous oven was always hapy on the 20A breaker.

    As Max capacity of this is 26A .... I need to find a solution for this Grid switch.
     
  4. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,361
    Thanks Received:
    387
    Location:
    Herefordshire
    Country:
    United Kingdom
    there is a youtube video on this coming soon!

    Fitting a contactor near the consumer unit to switch the oven (or hob) on and off. Clunk!

    Personally I consider it a crazy situation, just so a grid switch can be used!
     
  5. RickH

    RickH

    Joined:
    10 Dec 2008
    Messages:
    281
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    I can't find a Grid switch higher than 20A ..... I know I could increase breaker to 32A ... but would then need higher capacity grid switch
    Anybody any suggestions ?

    So far only thought is I would need to put a link in bypassing the GRID switch (and fit a blanking plate) and put a DP cooker switch instead of MK5045 connection point.
    Unless anyone else has a better idea.


    If my idea is the option what in neatest way to 'bridge' the 4mm t&e ... use WAGO connectors ...
    https://www.tlc-direct.co.uk/Products/WA412C.html They are good for 32A
    or WAGO push connectors rated at 40A
    https://www.tlc-direct.co.uk/Products/WA173.html


    Anybody experience of using these ? which is easiest to use ... or is there a better way

    Connection will be within confines of the 'back box' so all still protected.
     
    Last edited: 28 Aug 2019
  6. RickH

    RickH

    Joined:
    10 Dec 2008
    Messages:
    281
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    OK .. thanks, always thought DP local switch was requirement ... maybe as you see so many cooker switch boxes.
     
  7. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    8,236
    Thanks Received:
    1,513
    Location:
    Poole, Dorset
    Country:
    United Kingdom
  8. RickH

    RickH

    Joined:
    10 Dec 2008
    Messages:
    281
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    Unfortunately that would not be compatible with MK Grid system
     
  9. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    6,961
    Thanks Received:
    835
    Location:
    Dorset
    Country:
    United Kingdom
    What else does the grid switch serve?

    Are you not running a new separate supply for the oven then?
     
  10. RickH

    RickH

    Joined:
    10 Dec 2008
    Messages:
    281
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    No exisiting 4mm2 cable is big enough
     
  11. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,361
    Thanks Received:
    387
    Location:
    Herefordshire
    Country:
    United Kingdom
    watch from 4 minutes

     
  12. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    6,961
    Thanks Received:
    835
    Location:
    Dorset
    Country:
    United Kingdom
    What else does the grid switch serve??
     
  13. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,663
    Thanks Received:
    1,860
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Hmm. Quite a few cables zig zagging in that stud wall. May be >50mm deep though, but doesn’t look kosher to moi.
     
  14. daggermark

    daggermark

    Joined:
    11 Jul 2017
    Messages:
    87
    Thanks Received:
    8
    Country:
    United Kingdom
    That was exactly my thought. I'm not convinced they are deep enough, and they certainly aren't in safe zones.
     
  15. eveares

    eveares

    Joined:
    28 Jul 2012
    Messages:
    1,269
    Thanks Received:
    45
    Location:
    Surrey
    Country:
    United Kingdom
    My issue with using a contactor with a remote switch without also using a standard DP isolator is what happens if the contactor gets jammed on. Note that you would not use a domestic DP switch for safe isolation either as you can not lock them off normally.
     