Can't remember how many rads you have?.
It will take a lot of balancing to get that rad hot, you will probably have to compromise and accept a fairly slow heat up in this rad to allow reasonabe heat output from the remaining rads, the target flow temperature will probably also have to be increased to 70/75C, very unsatisfactory overall IMO,
All Vallient boilers (apart from the "4" series) have a internal bypass, the boilers come with this set to 250mbar, 2.5M, so this is the maximum head available (at this default setting) to circulate through all the rads, relatively quite low. it can be adjusted to a maximum of 350mbar, 3.5M which will be quite adequate for most systems, it may be worth looking at this but requires your installer to change it and also talk to Vallient re changing pump settings.
It will take a lot of balancing to get that rad hot, you will probably have to compromise and accept a fairly slow heat up in this rad to allow reasonabe heat output from the remaining rads, the target flow temperature will probably also have to be increased to 70/75C, very unsatisfactory overall IMO,
All Vallient boilers (apart from the "4" series) have a internal bypass, the boilers come with this set to 250mbar, 2.5M, so this is the maximum head available (at this default setting) to circulate through all the rads, relatively quite low. it can be adjusted to a maximum of 350mbar, 3.5M which will be quite adequate for most systems, it may be worth looking at this but requires your installer to change it and also talk to Vallient re changing pump settings.