I have been doing a lot of work to my property. I have got to the point of putting the down stairs radiators back on the wall.
At the moment they are all fed from 8mm microbore, since reinstalling them they barely get warm. I have bleed the system many times.
I have very limited access under the floor, I have inspected the pipes to find most of them crushed/kinked.
A few options i have come up with.
1, Due to limited access, using old pipes pull through more microbore pipe ( chance might get damaged)
2, Use old pipe to pull through 15mm speedfit pipe, and connect to a new manifold.
3, any other options.
The flow and return are both 22mm copper pipe.
Regards
Russell
At the moment they are all fed from 8mm microbore, since reinstalling them they barely get warm. I have bleed the system many times.
I have very limited access under the floor, I have inspected the pipes to find most of them crushed/kinked.
A few options i have come up with.
1, Due to limited access, using old pipes pull through more microbore pipe ( chance might get damaged)
2, Use old pipe to pull through 15mm speedfit pipe, and connect to a new manifold.
3, any other options.
The flow and return are both 22mm copper pipe.
Regards
Russell